How to Handle Forced Points and Manual Overrides in Building Advisor

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to Handle Forced Points and Manual Overrides in Building Advisor
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • David_Purser
    David_Purser
  • JonGreen
    JonGreen

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
928 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to Handle Forced Points and Manual Overrides in Building Advisor

Picard David_Purser Picard
‎2024-11-19 01:33 PM

Issue

Since the Cloud Plugin cannot perform search operations on EBO, Building Advisor can only estimate the number of forced points using the event log and, for EBO versions above 3.2.1, the server archive. 

Product Line

EcoStruxure Building Advisor

Environment

BMS Health

Cause

1. Incomplete Event Log: The event log may be incomplete if the maximum capacity is reached in EBO (events are rolling). When a customer connects their system, some historical events may be missed.
2. High Event Production: If a customer's system generates events at a higher rate than BA can process (currently, BA can ingest 100,000 events every 6 hours), some events may be overlooked, especially if there are many noisy events.
3. Understanding of Events: BA can only recognize forced and unforced events. BA will lose track of that point if an object's absolute path is updated or deleted instead of being unforced.
4. External Tools: BA cannot track it if an external tool forces a point without creating a corresponding forced/unforced event in EBO.

 

Limitations with EBO Versions 3.2.1 or higher:

Building Advisor can resolve issues for each server by retrieving snapshots from the server archive. This method can address the abovementioned issues, except for point number 4. Additionally, Bacnet points forced via commands are unavailable in the server archive, meaning we cannot retrieve those values through the Cloud Plugin.

BacnetObjectCommandTab.png

Resolution

  1. Check the EBO Version, and If the customer's system is older than version 3.2.1, advise them to upgrade.
  2. Verify Server Archive, ensure the issue pertains to Bacnet points, and proceed to the next step. Ensure all servers associated with the mismatched forced items have an updated server archive. This will enable the Building Advisor (BA) to obtain the correct snapshots from the system. You can check this in the building's BA connectivity tab. BAConnectivityTab.png
  3. If the servers are updated, proceed to the next step. If they are not, ensure that server backups are created periodically. You can check this in the BA architecture tab under the backup section. BABackupStatus.png
  4. If a newer backup is present compared to the "Last Upload" in the server archive table, attempt to send it again. Refer to the instructions on how to send a new backup at the end of the file.
    If there isn’t a newer backup, create one and send it. Important: Please note that it may take one to two days for the Building Advisor (BA) to reflect the updates.
  5. If the object exists in EBO, retrieve the events from the relevant branch and filter for force-type events. EBOForcedEventsInThisBranch.png
  6. If the last event is unforced and BA is showing as forced, Force it and then unforce it one time. If it was a Bacnet point, try to force it from the basic tab. EBOForceObjectBasicTab.png
  7. Note: If you have multiple points, you can search using the appropriate criteria and perform all the force/unforce operations simultaneously. EBOMassForce.png
  8. If the object no longer exists in the path, you can create a replica of the object in the same path and perform the force/unforce operation. Ensure that events are created for your actions (see Step 5).

  9. If the point does not exist for manual override and you cannot set a new device in the path, please open a PSS case.

  10. Send a new backup using the following process:
    1. Navigate to ~/System/Modules/CloudPlugIn/Statistics/Services
    2. Add the Service type and Server name columns in the list view
    3. Locate the Service Type of SystemDiscovery, multi-select the server(s) affected, right-click, and select Execute task now
  11. If the issue is unresolved two days after uploading the updated SystemDiscovery files, please open a PSS case.
Labels (1)
Labels:
  • EcoStruxure Building Advisor
Tags (2)
  • Find more articles tagged with:
  • DavidPurser24
  • JonGreen24
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of