Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Launch of Consumer/Home Owner registration process!
We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.

How often are online/offline polls done for Modbus and MBus devices?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How often are online/offline polls done for Modbus and MBus devices?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • PeterLarsen
    PeterLarsen
  • DavidFisher
    DavidFisher
  • HenrikTarpgaard
    HenrikTarpgaard
  • Benji
    Benji
  • Sacco
    Sacco
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2937 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How often are online/offline polls done for Modbus and MBus devices?

Picard Product_Support
‎2018-09-06 10:39 AM

Last Updated: Spock PeterLarsen Spock ‎2022-08-21 08:47 PM

Issue

Needs to know how often Vista (or Xenta Servers) do online/offline polls for Modbus and MBus devices

Product Line

TAC Vista

Environment

  • Xenta Server
  • Modbus
  • Mbus

Cause

The devices may go offline for several different reasons. It's not possible to give a precise answer to this question, since it depends on your setup and the number of devices.

Resolution

In general, if a Modbus device has been detected as offline by the Xenta Server, it will wait 60 seconds until it tries polling that device again. That doesn't mean that a device will come online after 60 seconds if it has been offline because as described below, other factors comes into play, such as the number of devices and registers, and invalid registers.

Mbus:
The Mbus protocol is designed so that all information in the device will be received at every poll, regardless of what is defined in the device template. If the Xenta Server doesn't receive any information it will retry twice and if still no reply it will set the device to offline.
All offline devices will be transferred to an offline queue in the Xenta Server, and at every new poll one device (the oldest) will be moved to the poll queue again.
The reason for not retrying all is that if you have lots of devices that are offline at the same time, each poll would take very long time to complete and if using a short poll interval it may not be finished in time before the next poll. That will also mean that if you have many offline devices and have set a long poll interval in Xbuilder (default 1 min) it may take quite a while until all devices are online again.

Note: In Xbuilder 5.1.9 and later it's possible to set the number of offline devices to poll each cycle. In some cases, for example when there are few meters and/or long poll times you may want to increase this number.

Modbus/TCP:
You will have a Server address for the TCP Client and if that server's ip address can't be reached all the Modbus devices below it will go offline. However as soon it can be reached again (will be tried constantly), it will scan all devices below it, and if they reply they will be set to online.
If there's no response from a single device, it will retry twice before it's set to offline. The time it will take depends on the slave timeout setting in Xbuilder (default 3 seconds). As for Mbus, you have an offline queue where 1 device will be moved to the poll queue every poll cycle. The total poll time also depends on how many devices and registers you have defined (many devices/registers = longer poll time = longer time to detect if a device is offline/online).

Modbus/RTU:
It works similar to Modbus IP, except for the server part (which is not present).
Besides that, you also have the "transmit delay" setting in Xbuilder (default 0 ms, max 1000 ms) which may effect the time it takes for a device to be reported as online/offline

Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 12570
  • PeterLarsen22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore