Information about the number of socket connections Modbus TCP/IP uses to interface with other gateway / devices
  • Information about the number of socket connections Modbus TCP/IP uses to interface with other gateway / devices
  • Ramaaly
    Ramaaly
  • SangKim
    SangKim
‎2018-09-06 01:56 PM
Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2025-09-03 10:57 AM
Does Modbus TCP/IP xDriver opens socket connection per each device or the gateway of the devices?
Andover Continuum
  • NetController - CX9900, CX9940, CX9680.
  • Continuum bCX9640 (Infinet)
  • Continuum bCX4040 (BACnet)
As some Modbus TCP/IP gateways have the limitation of maximum TCP/IP connections, if Modbus TCP/IP xDriver opens a socket per modbus device and keeps it open, the gateway might run into a problem due to the limited number of socket connections.
The Modbus TCP/IP xDriver opens one(1) socket connection per server not device.
So for a gateway that has a number of devices, the Modbus TCP/IP xDriver only uses one(1) socket connection.