Issue
Need to connect xPModule away from the b3/i2 controllers. Need to know what is the maximum distance it can be installed using a ribbon cables.
Environment
Infinet II (i2) or BACnet (b3) families: i2/b3 920, i2/b3 810, i2/b3 814, i2/b3 850, i2/b3 851, or i2/b3 853.
The bCX1 Controller/Router models.
Cause
There is a limitation of the length of the cable being used.
Resolution
Either the 3-foot or 10-foot ribbon cable can be used. A total of 10 feet of cable may be used for all Expansion Modules.