Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

How is extended log data handled during time changes like daylight savings?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How is extended log data handled during time changes like daylight savings?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Nava
    Nava
  • BillNeville
    BillNeville
  • PaulFr
    PaulFr
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2010 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How is extended log data handled during time changes like daylight savings?

Picard Product_Support
‎2018-09-10 10:57 PM

Issue

Do extended logs have accurate entries for the spring and fall time change periods?  

Environment

CyberStation, all Continuum controllers, extended logs, controller logs.

Cause

What happens to extended log data during time changes?

Resolution

When the clocks are turned back, log data in the controllers will not be updated for the time interval of the change and therefore that data will not be collected by the extended logs.

When the clocks are turned forward, log data in the controllers is logged twice for the time interval of the change and therefore that data is collected twice by the extended logs.  

This occurs due to the fact that each log entry in the controller does not consist of a value and a timestamp. The timestamp we see in a report is calculated by the time of the last log entry (LastLogTime) in conjunction with the configured logging interval (LogIntervalSecs). This mathematical calculation saves memory in the controllers.

Extended logging is the mechanism most sites use to store, and report on data that is in excess of the amount of data stored in a controller. The extended log engine automatically collects the controller log data before it is overwritten. An added benefit of using extended logging is that the data can be easily backed up via several strategies such as database backups and/or running extended log archiving applications. In the controllers, not only is the memory limited, but the data is stored in volatile RAM, so extended logging is a more robust and long term strategy of collecting and storing the data.

Extended logs can be set up on any of the automatic log types (LogInstantaneous, LogAverage, LogMinimum, LogMaximum). 

During a period when the clock is moved forward, (for example, 2:00am Sunday March 11, 2012 on the east coast of the US), reports may display timestamps that essentially never existed (in this example 2:00am to 2:59:59am). It is recommended that these entries are simply ignored or crossed out.

The period when the clock is moved backward is more difficult, if it is critical that data be captured for the duplicated time. An example is Sunday November 4, 2012. At 2:00am on the east coast of the US the clock is set back one hour. This means that the times from 1:00am to 2:00am occur twice. However, extended log reports will only show one set of data for the reason described above. The reports will show the first 1:00am to 2:00am data; the second 1:00am to 2:00am data needs to be captured separately. 

If point log data must be captured for the duplicated timeframe, additional point configuration and Plain English (PE) programming must be used to capture and timestamp the realtime data values for the duplicated timeframe. This involves creating a numeric with a manual log  for each critical point which mirrors the live data value of the affected InfinityInputs, InfinityOutputs and InfinityNumerics. In addition, an InfinityDatetime point with a manual log must be created, one in each controller for each different loginterval of the points being mirrored in that controller. The PE program(s) capturing the point values will write the controller's date system variable to this InfinityDatetime at the same time it writes the live point value, thereby creating a timestamp that will be used for reporting. The last step will be writing the mirrored points and their corresponding timestamps to a file on disk and then printing and/or backing up that file for redundancy. 

Click here to download a zip file containing sample dump files and a readme. This is an example of one way to accomplish the above data capture. 

Labels (1)
Labels:
  • Andover Continuum
Attachments
DLST Fallback Data Archive App.zip
Tags (4)
  • Find more articles tagged with:
  • 11602
  • bst
  • dst
  • gmt
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore