How is a TC900 configured to use a 3-wire (floating) valve actuator?
  • How is a TC900 configured to use a 3-wire (floating) valve actuator?
  • RobertAndriolo
    RobertAndriolo
  • CraigEl
    CraigEl
Administrator CraigEl Administrator
‎2020-09-09 12:48 AM
on ‎2020-09-09 12:48 AM
The documentation notes a TC900 can be changed from a 4-pipe system with a 2-wire motorized valve to a 2-pipe system with a 3-wire motorized valve. What parameter changes are required?
Field Devices
  • TC907-3A4LAB
  • TC907-3A4LMAB
  • TC907-3A4DLSAB
  • TC907-3A4DLMSAB
  • TC907-4FMSAB
  • TC907-3A4DPSAB
  • TC907-3A4DPMSAB
  • TC907-3A4DPMSA-24B
  • TC907-4FMSA
  • TC907-3A4LMA
  • TC907-3A4LA
  • TC907-3A4DPSA
  • TC907-3A4DPMSA-24
  • TC907-3A4DPMSA
  • TC907-3A4DLSA
  • TC907-3A4DLMSA
Documentation is unclear in how a TC900 is configured to use a 3-wire valve actuator
  • Access the parameter settings by pressing and holding the mode button for six seconds during thermostat power up.
  • Press the mode button or Fan button to move forward or backward between the parameters until parameter 09 is displayed.
  • Press the up and down buttons to set the parameter to 04.
  • Field Devices
Tags (2)
  • CraigEllis20
  • TC900
100% helpful (4/4)