How does the controller determine which workstation will log the alarm into the SQL database when using "Enhanced Alarm logging"?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How does the controller determine which workstation will log the alarm into the SQL database when using "Enhanced Alarm loggi...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • GavinHe
    GavinHe
  • ScottLeedberg
    ScottLeedberg
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1114 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How does the controller determine which workstation will log the alarm into the SQL database when using "Enhanced Alarm logging"?

Picard Product_Support
‎2018-09-06 02:58 PM

Last Updated: Admiral GavinHe Admiral ‎2023-05-03 08:43 AM

Issue

How does the controller determine which workstation will log the alarm into the SQL database when using "Enhanced Alarm logging"?

Product Line

Andover Continuum

Environment

  • Workstation
  • Enhanced Alarm Logging

Cause

Alarms will be delivered by a NetController to all Workstations that have Ids between 191 and 254 assuming a teach was done. The first Workstation to receive the Alarm will log it in the Database. There is a ratcheting algorithm that is used by the NetController to determine which Workstation will be the first one to receive Alarms. In many applications, it is necessary to control which workstation will be the first to receive the alarm and log it in the Database. Knowing how the algorithm works provides the ability to design a system with a designated alarm logging workstation.

Resolution

The algorithm is as follows:

  • The Netcontroller will take its own AccNetid and mask it with 63 stripping off the 2 high bits of its id leaving a result in the range of 1 to 63.

Further explanation of the binary masking:

  • NetControllers with Ids between 1 and 63, result is their ID.
  • NetControllers with Ids between 64 and 127, result is their ID - 64 (ID range of 0 to 63).
  • NetControllers with Ids between 128 and 190, result is their ID - 128 (ID range of 0 to 62).

That result is then added to 190 and that is the ID of the first Workstation to get the Alarm and Log it in the Database.

If there is not a Workstation with that ID (or the workstation with that ID is offline), the NetController will send the alarm to the Workstation with the next highest ID above the one calculated by the ratcheting algorithm. If none of the Workstation Ids are higher than the one calculated, the routine will loop around and use the lowest Workstation ID to send to the first.

Example 1:

NC1, id1
NC2, id2
NC3, id3

WS1, id191
WS2, id192
WS3, id193

Result of ratcheting routine:
NC1 sends to WS1 first
NC2 sends to WS2 first
NC3 sends to WS3 first

Example 2:

NC1, id1 1+190=191
NC2, id2 2+190=192
NC3, id3 3+190+193

WS1, id201
WS2, id202
WS3, id203

Result of ratcheting routine:
NC1 sends to WS1 first
NC2 sends to WS1 first
NC3 sends to WS1 first

Example 3:

NC1, id101 101-64=37, 37+190=227
NC2, id102 102-64=38, 38+190=228
NC3, id103 103-64=39, 39+190=229

WS1, id191
WS2, id192
WS3, id193
Result of ratcheting routine:
NC1 sends to WS1 first
NC2 sends to WS1 first
NC3 sends to WS1 first

Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 2566
  • GavinHeward23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of