Issue
How do I set the Tap emulation for a Process Control Unit (PCU)?
Product Line
TAC INET
Environment
- Process Control Unit (PCU) 7716/8
- Process Control Unit (PCU) 7756
Cause
Need to set TAP Emulation type on PCU
Resolution
- Using the HHC, press [Code], 90 [Enter]
- Press [Inc] or [Dec] through 7801, 7803, 7806 Tap emulation
- Press [Enter] to accept your choice
- 7801 for direct connection and Integrated dial operation
- 7806 for direct connect, integrated dial, and ADAA
For additional details, please see the following documentation: