Issue
Product Line
TAC IA SeriesEnvironment
Niagara R2 Microsmart Service
Cause
Resolution
-
Maintain Recommended Poll Always Count
- Set Poll Always count to 250 (recommended level).
-
Adjust Cycle Time
- Check
averageExecuteTimein Poll - Status tab. - Increase
cycleTimein Poll - Config tab to matchaverageExecuteTime + 1 secondto prevent overruns.
- Check
-
Optimize Minimum Poll Interval for Shadow Objects
- Review
minimumPollIntervalfor each Microsmart point shadow object. - Increase from default 1000 ms where possible.
- Example: For space temperature shadow objects, set between 30,000 ms to 60,000 ms.
- Review
Recommended Settings
| Parameter | Recommended Value | Notes |
|---|---|---|
| Poll Always Count | 250 | Prevents excessive polling load |
| Cycle Time | Avg Execute Time + 1 sec | Adjust based on Poll - Status tab |
| Minimum Poll Interval | 30,000–60,000 ms (for temp) | Increase from default 1,000 ms where possible |