Issue
Product Line
TAC IA SeriesEnvironment
Niagara R2 WorkPlace Pro
Cause
Resolution
To change the nciMinFlow value:
- Copy and paste the DynamicCmd object from:
Local Library\tridiumx\lonworks\conversioninto the Workspace. - Link the nciMinFlow property on the VAV shadow object to the Link property on the DynamicCmd object.
- In the Config tab of DynamicCmd properties, set
floatConversionas:- 1st dropdown: Volumetric Flow
- 2nd dropdown: liters_per_second
- 3rd dropdown: cubic_feet_per_minute
- In the Visual tab, type MinFlow in the float box and apply changes.
- Switch to Monitor mode, right-click the DynamicCmd object, select MinFlow, and enter the desired value in CFM.
- The nciMinFlow SNVT in the VAV controller will update accordingly.