Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

How can a BACnet system be customized to maximize data throughput? The site has a Niagara R2 Enterprise Server and a UNC with a variety of MSTP controllers connected to the UNC.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How can a BACnet system be customized to maximize data throughput? The site has a Niagara R2 Enterprise Server and a UNC with...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl
  • sesa119747
    sesa119747
  • sesa116877
    sesa116877

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1543 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How can a BACnet system be customized to maximize data throughput? The site has a Niagara R2 Enterprise Server and a UNC with a variety of MSTP controllers connected to the UNC.

Picard Product_Support
‎2018-09-07 12:52 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-28 07:00 PM

Issue

How can a BACnet system be customized to maximize data throughput?  The site has a Niagara R2 Enterprise Server and a UNC with a variety of MSTP controllers connected to the UNC.

Environment

  • Niagara R2 Enterprise
  • UNC
  • MSTP controllers

Cause

Improper configurations won't achieve optimum performance.

Resolution

This can be a relatively complicated question, however, there are a number of basic steps that can be taken in terms of best practices to enhance performance.

Within the UNC station, any BACnet objects that are not needed are to be deleted. During the learn of a BACnet controller, many objects are learned that are not used.
All BACnet objects when learned into a station are placed in Poll-Always containers. All but the most critical objects, schedules and trended objects are to be moved to Poll-on-Demand containers.

All controllers on the MSTP bus should be consecutively addressed.  Gaps in addressing add delay in communications.
The MaxMaster setting in all controllers, including the UNC, is to be set to a numeric value two greater than the highest MSTP controller address on the network. To leave MaxMaster at 127 but only have 20 controllers on the network will also add delays in communications looking for the other non-existent 107 controllers.

The MaxInfoFrames setting in the UNC or MNB-1000 is to be set to a number higher than 5 but no more than 20. This setting determines how many pieces of information can be requested each time the UNC or MNB-1000 receives the token on the MSTP bus. The default value is 1 and if left at this value the system will be sluggish with updating values on graphic screens. The range of 5 to 20 is given as a starting point for experimenting and each system will be different depending on the number of controllers and what data is being requested.  Lab tests have shown there is a performance curve with an optimum point.  Starting at a value of 5, performance increases as the value increases.  Performance will then peak and any further increase to the setting will result in a performance reduction.  As a result, stay above 5 but less than 20.

Refer to the document titled "I/A Series MicroNet BACnet Wiring, Networking, and Best Practices Guide" (F-27360) for additional information.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 2652
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now