Issue
Product Line
TAC IA SeriesEnvironment
- Niagara R2 UNC
- BACnet network
Cause
Resolution
- Configure the Niagara R2 UNC as a BBMD device.
- In the Commissioning Tool, set up communications so that the computer accesses the remote BACnet network using the IP address of the UNC configured as BBMD.