Groups within Groups
  • Groups within Groups
  • Roger_Bently
    Roger_Bently
‎2018-09-06 02:48 PM
Are you trying to implement Groups within Groups and it is not functioning as programmed?
I/NET Access
The term “Groups within Groups” is where a user has access on one group e.g. 5-7 Mon-Friday but needs to get in on a Saturday but the application is permanent. So a Secondary schedule would not be applicable here, since this is only for a temporary period.
To create a “Group within Group” application the following steps need to be followed:
  1. Go to Access Doors, select the door or doors that will have this Saturday schedule so that the group when created can access this schedule.
  2. Once created, exit out of this editor and go to Access Groups.
  3. Create a group that has access to the doors that will have access on the Saturday Schedule. All other doors need to be set to Unselect, close this editor.
  4. Now go to the main group that this group will be part of to create the “Groups within Groups” schedule.
  5. Modify the group and select Doors/Groups and now select the group that has the Saturday schedule on it. Keep in mind that the only schedule for the doors would be the Group Schedule; the Primary Schedule should be set to Unselect.
  6. If a Primary Schedule is selected, then it will take precedence over the Groups within Groups Schedule and would negate the application.
  • TAC INET
  • 3046