Graphical indicator for a Niagara AX or N4 BACnet object to show when a point is overridden.
  • Graphical indicator for a Niagara AX or N4 BACnet object to show when a point is overridden.
  • RandyDavis
    RandyDavis
  • WaynePeters
    WaynePeters
  • sesa119747
    sesa119747
‎2018-09-06 02:40 PM
Last Updated: Guinan RandyDavis Guinan ‎2023-05-25 11:41 AM
Can a graphical indicator be placed on a Niagara AX or N4 view to indicate when a point is overridden, analog or binary?
TAC IA Series
  • I/A Series AX graphics
  • I/A Series N4 graphics
By default, the StatusEffect setting is turned off (None). Change StatusEffect to Color to enable the graphical indicator.
In the properties of the BoundLabel, set the StatusEffect attribute to Color (default is None). This will cause the object to turn purple (the default color) when it is overridden.