Graphic, Dynaview, Actipane Alarm and Logging Data Stops Updating

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Graphic, Dynaview, Actipane Alarm and Logging Data Stops Updating
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1194 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Graphic, Dynaview, Actipane Alarm and Logging Data Stops Updating

Picard Product_Support
‎2018-09-09 09:27 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-20 11:46 PM

Issue

After a period of operation, graphics, Dynaview, Actipane, alarm, and logging data may stop updating in Sigma systems.

Product Line

Satchwell BAS & Sigma

Environment

Satchwell Sigma

Cause

This issue is typically caused by the controller communication buffer not clearing. A common scenario is when engineers temporarily use their laptops as Sigma servers and later disconnect them without disabling logging or alarm routing. As a result, data continues to be routed to non-existent servers, causing the buffer to fill up.

Resolution

Follow these steps to resolve the issue:

  1. Check Controller Alarm Buffer

    • Perform a controller stat (F3) to verify if the alarm buffer is retaining data.

  2. Attempt to Clear the Buffer

    • Use the ‘Request Deferred Logs and Alarms’ function.
  3. If Unsuccessful, Proceed with the Following Checks:

    • Ensure logging and alarm routing information is correct for the active server.
    • Verify the tolerance settings for analogue object values.
    • Confirm that controller backup/default servers are correctly configured.
  4. Clear the Controller Archive

    • Use the SDCU utility (Advanced option) to clear the archive.
  5. Cold Start the Controller

    • Perform a cold start and allow the server files to download again.

Additional Notes

  • Always ensure temporary servers are properly decommissioned by stopping any active logging or alarm routing before disconnecting.
  • Regularly monitor controller buffers to prevent data loss or system lag.
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (2)
  • Find more articles tagged with:
  • 5232
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore