Getting "Card Bad Parity" or incorrect card numbers from a Wiegand Card reader in Continuum

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Getting "Card Bad Parity" or incorrect card numbers from a Wiegand Card reader in Continuum
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • David_Kendrick
    David_Kendrick
  • PaulFr
    PaulFr
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4405 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Getting "Card Bad Parity" or incorrect card numbers from a Wiegand Card reader in Continuum

Picard Product_Support
‎2018-09-06 02:11 PM

Last Updated: Admiral David_Kendrick Admiral ‎2023-05-04 02:32 AM

Issue

When swiping / presenting a card to a Wiegand card reader in Continuum it does not open the door..  When opening a Listview of Events the log shows "Card Bad Parity" or it reads an incorrect card number using Custom Wiegand.

Product Line

Andover Continuum

Environment

CyberStation all versions, with any of the Access Controllers - ACX700, ACX780, ACX57xx, NetControllers with any of the AC1 module range.

Cause

This fault is caused by incorrect wiring to the reader or choice of a 3rd party reader that is not compatible with Continuum.

Resolution

When wiring between a controller and a Wiegand card reader, all wires must be connected straight through to the corresponding terminal.

  1. Data1 to Data1
  2. Data0 to Data0,
  3. Gnd to Gnd ..............etc.
  4. See relevant controller installation guide for further details on reader wiring and cable types.
  • On HID readers be sure to wire between the two Data 1 terminals and the two Data 0 terminals. Do not refer to the Clock and Data legend that is also on the controllers and many readers, as this is only used for ABA data connections.
  • When using a separate Power supply for the reader, the 0V (Ground) terminal must still be connected back to the controller GND terminal to ensure both devices are working from a common ground potential.
  • When testing out cards and readers always use a Listview showing a relevant Event log, as this will provide more information than the event view from the Door editor itself.
  • To assist with troubleshooting data reads by the controller especially when using Custom Wiegand for non standard Continuum formats:
    1. Select only Custom Wiegand in the Door configuration.
    2. Rename the "AccessFormat" array if one has been created.
    3. Present a card to the reader.
    4. Check the Listview for Events as this will show the raw binary data string the controller is receiving.
    5. Compare raw binary data against the expected data from the reader used.
Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 4502
  • DavidKendrick23
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore