Getting error message of "Unsupported feature" and compile / check PE program and cannot save it.
  • Getting error message of "Unsupported feature" and compile / check PE program and cannot save it.
  • SangKim
    SangKim
‎2018-09-06 01:26 PM
When saving a PE program that uses embedded Continuum functions such as SendEmail() , it errors when checking / compiling the program and shows the error message of "Unsupported feature".
Netcontroller (CX9xxx)
InfinetController(i1 , i2xxx)
BACnet controller (BCX, b4920, b3xxx)
This happens when using the controller specific functions such as SendEmail() in the Program object not the InfinityProgram object.
Create a new InfinityProgram object in the controller , copy the source code and save.  It will check successfully and save the program in the controller. After it is saved successfully, delete the problematic Program object from the controller.