Getting Errors when attempting to open WebReports

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Getting Errors when attempting to open WebReports
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • David_Kendrick
    David_Kendrick
  • DavidFisher
    DavidFisher
  • Derrick_Ratliff
    Derrick_Ratliff
  • Benji
    Benji
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3482 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Getting Errors when attempting to open WebReports

Picard Product_Support
‎2018-09-11 05:27 AM

Last Updated: Admiral David_Kendrick Admiral ‎2023-04-25 06:26 AM

Issue

Users are getting two possible errors when trying to open WebReports page

Error #1 - "The Web Site URL for Reports is not configured. Please contact the administrator"

Error #2 -  "The webpage cannot be found" can also be generated.

Product Line

EcoStruxure Building Operation

Environment

Web Reports

Cause

These Errors can occur when the link to the Reports Server is not correct.  This is usually caused by having the Enterprise Server and Report Server on the same PC

It should be noted that having both the Enterprise and Report Server's on the same PC is not recommended.

 

The reason the Workstation can not access the Web site / Web service URL's is because the Report Manager points to the "Localhost".  When you try to use a Workstation that is not local to the Report Server it can not locate this URL, hence the error.   This issue is not seen if when installing the Report Server on a different machine to the Enterprise Server as designed.

Resolution

Even though the Enterprise Server is local to the Report Server if access required by any other Workstation or WebStation you must enter the IP or PC Name of the Report Server within the Report Manager's Web site URL.  In this instance changing only the Web site URL will rectify the problem but it is recommended to change both the Web site and Web Service URL settings. This will allow any remote Workstation / Browser to find the Report Server.

  1. In workstation, Browse, to the System folder
  2. Click on System>Report Manager
  3. Set the Web site URL to http://localhost/SchneiderElectric/WebReports/Login.aspx
  4. Set the Web Service URL to http://localhost/SchneiderElectric/WebReportsService
  5. If the Enterprise Server resides on a different PC than the Reports Server, change "localhost" to the Report Server computer name or IP address

After making this change WebReports should display correctly:

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • 13749
  • 404
  • DavidKendrick23
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore