Issue
Get "invalid address" when reading values from a Modbus device in Vista.
Environment
- Vista 5.1.X
- XBuilder
- Modbus
- Xenta 5xx / 7xx / 9xx
Cause
This problem can be caused by the Modbus device name and the Modbus interface name having the same name in the XBuilder project.
Resolution
If the Modbus device and interface have the same name change one of them to be different from the other.