Can the GV sensor be connected to the TAC Xenta controller using Analog Input signal?
TAC Vista, Field Devices
  • Xenta 401
  • Xenta 301
  • Xenta 281
  • Xenta 121
  • Xenta 122
The GV sensor is non-electrical itself and needs a VAV controller to measure the air velocity transferred from the sensor.
The 224V and 224VL that are listed in the GV documentation, are both obsolete and no longer available. The Xenta 102ES, part no. 007305370, is designed to work with the GV sensor.