Further techniques to use for debugging Script programs

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Further techniques to use for debugging Script programs
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4294 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Further techniques to use for debugging Script programs

Picard Product_Support
‎2018-09-06 08:24 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:42 AM

Issue

Use of the Building Operation Script editor and general Script programming is covered in the Training courses and technical reference guide, what other techniques can be used to debug a program?

Product Line

EcoStruxure Building Operation

Environment

 Building Operation Script editor.

Cause

Often additional techniques are required to debug Script programs, especially when attempting to analyze, modify or fault find other people's code.

Resolution

Some techniques you can use for debugging your program and isolating problems are:

  1. Add in additional line labels to the program to isolate where the program is disabling or failing, if it disables you will be able to see the "CurrentLine" it has failed on and therefore know which line of code is causing the problem.
  2. Use the Trace feature to step through a program and monitor the binding variables, stepping through each line of code to ensure the values are all set as expected.
  3. Even if a program does not disable you can use the "Stop" keyword in the program, it will act as a break in the code and you can look at the values of the various variables, this may be a useful alternative to the Trace feature.
  4. Use the Watch window and the Binding Variables window to show the values of the various objects, when used with the above two techniques it allows you to accurately trace a program flow.
  5. Ensure all of the code used is compatible with the Script programming rules and that Continuum Plain English programs are not just used without conversion. Check the Plain English and Script Difference Guide.
  6. For programs in an i2 or b3 controller, ensure none of the Program size limitations are exceeded, see Plain English program limitations on number of characters in program and line labels.
     
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • 19985
Was this article helpful? Yes No
0% helpful (0/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore