Full process for properly configuring Vista Alarms

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Full process for properly configuring Vista Alarms
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Jonas_Brissman
    Jonas_Brissman
  • DavidFisher
    DavidFisher
  • Derrick_Ratliff
    Derrick_Ratliff
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1778 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Full process for properly configuring Vista Alarms

Picard Product_Support
‎2018-09-06 02:06 PM

Issue

Problems with alarms or configuring alarms in Vista

Environment

TAC Vista Workstation

Cause

Improper alarm configuration

Resolution

Here are steps to configure each part of the Alarm  in Vista.

Change of State Object - This is the source of the alarm.

  1. Right click on a folder in Vista and select New > Object > Change of State
  2. Name the object
  3. Double click on the object to modify it
  4. Provide a description of the alarm and set a priority level if required.
  5. Click on the Object Tab and select the Object to Monitor and the Reference property
  6. Click on the Alarm Tab
  7. Select an Alarm processing control.  These should be located under the TAC Vista Root object. The default is $Alr_Cntrl
  8. Fill in the appropriate text field.  Note: "Text for" fields are text issued as the result of the alarm. "Triggering" text should only be used when monitoring a string value.
  9. Set Low and High Limit for the alarm to occur
  10. Set Minimum change: This is the smallest deviation required to trip an alarm when using numeric values.

Alarm Receiver Objects - These objects route alarms that are intended to go outside of Vista. There are 3 types: Print, file, and Mail (email)

  1. Right click on a folder in Vista Workstation and select New>Object>Alarm Receiver - E-Mail (or applicable type
  2. Name The Object
  3. Double Click on the Object to modify it
  4. In the General Tab provide the description and appropriate information for your alarm type (email recipient)
  5. In the Alarm Fields Tab, select the fields you wish to appear in the printout or email
  6. If you are using Alarm Receiver - Video you will need to set the video settings in the General tab and select cameras to record in the Video Cameras Tab
  7. Click Okay

Alarm Control Group - This allows us to control distribution of an alarm.  Multiple control Groups will allow multiple distribution lists. 

  1. From Vista Workstation, right click on the TAC Vista folder (Alarm Control Objects can only be created here)
  2. Select New > Object > Alarm Control
  3. Name the Object
  4. Double Click on the Object to modify it
  5. Enter a description
  6. Click "Add" and browse to the desired Alarm Receivers
  7. Click on the Acknowledge tab and configure appropriate parameters
  8. Click on the Time Control
  9. Here you can browse to a time variable that will determine when to use the Alternate Receivers list
  10. Add Alternate receivers
  11. Click OK
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4681
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore