Forcing points to export in Continuum Infinet Integration in EBO

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Forcing points to export in Continuum Infinet Integration in EBO
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • JohnBoehmer
    JohnBoehmer
  • AbeMeran
    AbeMeran

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3049 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Forcing points to export in Continuum Infinet Integration in EBO

Captain AbeMeran Captain
‎2019-04-02 12:50 PM

Issue

The value of an exported Infinet point is not updated in some or all of the subscribing controllers.

Product Line

EcoStruxure Building Operation, Andover Continuum

Environment

  • Building Operation Automation Server
  • Continuum i2 Controller

Cause

The subscribing controller is offline or inaccessible when the IE update is broadcast.

Resolution

The main disadvantage with the Continuum Import/Export (IE) system is that, in certain cases, it is possible that the updated value may not reach one or more of the subscribers due to various reasons such as network or controller down problems, excessive traffic on the network, etc.

This is not of big concern when the point is of an analog type that changes frequently such as a temperature input since the point will update again when the temperature changes in a matter of seconds or minutes at the most.  For binary values though, a missing update is a big concern.

Consider an occupancy schedule point that turns ON at 08:00 and off at 17:00.  If a subscriber misses the 08:00 update the zones under control by the subscriber will be unoccupied the entire day.

The Point’s Refresh Attribute.
Continuum points have a ‘Refresh’ attribute that is used to force the IE system to send a new updated value, setting the refresh attribute to true forces the Infinity controller to export the point’s value regardless of whether it has changed or not.

It is IMPERATIVE that a PE program periodically refreshes binary points that are exported in Infinity controllers such as i2 devices.

In the schedule example described above, a program* can be added to the Infinet controller that hosts the exported point.  This program should be triggered by the minute system variable and coded as follows:

Refresh Program.jpg

*make sure the program is of the type Infinet Script Program

This will ensure that any subscribers to the schedule OCC flag won’t go more than a minute with a stale value of the point.

Refreshing points that reside under the Infinet interface of the Automation Server (EBO 3.1 and greater)

If the point to be refreshed resides under the Infinet interface of the AS-P then there are some differences in the way the refresh is accomplished.

  1. The program will be of the type Script Program.
  2. The point will have a REFRESH property, you bind to the refresh property in the Script Program instead of the point's value.
  3. The most important difference is that while in the i2 device the export takes places when you set the value of the refresh property to true, in the Automation Server the export takes place when the value of the refresh flag is toggled, regardless of the value (true or false)

Below is an example of a Script Program refreshing some value objects that reside at the Automation Server under the Infinet interface

The statement DigValue1 = (DigValue1 = false) is just a very efficient way to toggle the value of the refresh property, it is equivalent to saying.... If DigValue1 = false then set it to true and if DigValue1 = true then set it to false.

IE_RefreshProg_SVR.PNG


Things to consider when refreshing exported points.

  1. Do not refresh points at a fast rate as this will cause unnecessary traffic on the Infinet field bus, refresh rates of one minute or more are strongly recommended.
  2. For the same reason, when refreshing many points, the operation should be staggered to avoid flooding the Infinet bus with an avalanche of IE traffic at the same instant.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (4)
  • Find more articles tagged with:
  • AbeMeran19
  • AbeMeran20
  • ie
  • infinet
Was this article helpful? Yes No
100% helpful (3/3)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of