FieldServer LON Device Binding Fails in Niagara R2 – Service Type Error
Building Automation Knowledge Base
Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
A FieldServer device was successfully commissioned in a Niagara R2 station using LON. However, the Lon Link Manager shows all related bindings with a status of service_type_error, and none of them will bind.
Product Line
TAC IA Series
Environment
Niagara R2 station with LON integration using FieldServer device
Cause
Most FieldServer devices using LON require a different service type than the default standard binding type. Using the incorrect service type prevents successful binding.
Resolution
Change the binding type from standard to critical in the Lon Link Manager, then attempt to bind the devices again.