Field Devices - Wiring a MD10B-24 / MD20B-24 actuator to a Climatronic CXT / CXR / CSC Actuator
  • Field Devices - Wiring a MD10B-24 / MD20B-24 actuator to a Climatronic CXT / CXR / CSC Actuator
‎2018-09-10 08:58 PM
Last Updated: Crewman ContentModerator ‎2025-08-11 04:05 AM
  • MD10B-24
  • MD20B-24
  • Actuator
  • Climatronic
  • CXT
  • CXR
  • CSC
The Climatronic controller switches the O volt side of the 24 volt supply, but the actuators shows that it requires 24 volts to open and close.
The Satchwell range of Climatronic controllers have always switched the 0 volt side of the 24 volt supply to control the actuator position.
CXT Controller - Terminals 13 and 14 provide 0 volts to close or open the actuator. A permanent 24 volts is provided by terminal 37.
For the complete datasheet, please click HERE.
CXR Controller - Terminals 23 and 24 provide 0 volts to close or open the actuator. A permanent 24 volts is provided by terminal 37.
CSC Controller - Terminals 33 and 32 provide 0 volts to close or open the actuator. A permanent 24 volts is provided by terminal 37.
The MD10B-24 / MD20B-24 datasheet shows the wiring as follows;
For the complete MD10B datasheet, please click HERE.
For the complete MD20B datasheet, please click HERE.
The above actuator wiring shows a 0 volt connection to the common connection (1) and a switched 24 volt connection (2 or 3).
To connect the MD10B-24 / MD20B-24 actuator to any of the above controllers it will be necessary to connect the actuator as follows.
  • Controller 24 volt  (37) to connection wire (1).
  • Controller Open signal (14, 24 and 32) to connection wire (2).
  • Controller Close signal (13, 23 and 33) to connection wire (3).
Please note that the actuator direction can be changed by repositioning the switch on the front of the actuator.