Field Devices - Where is the 0-10 volt control signal connected, on a Forta actuator?
  • Field Devices - Where is the 0-10 volt control signal connected, on a Forta actuator?
  • sesa125819
    sesa125819
‎2018-09-06 12:43 PM
Forta
M400
Actuator
Wiring
Connections
The customer was uncertain how to connect the M400 actuator.
The general configuration and connection details are the same for all of the Forta range of actuators.
All of the range can accept a 0-10 volt dc input or increase/decrease signals.
Terminal Function Designation
G                  24 V AC Supply
G0                24 V AC return
X1                 Input
MX                Input, neutral
VH                Increase
VC                Decrease
G1                16 V DC Supply for RC
Y                   0–100 % Feedback signal
The 0-10 volt control signal is connected to (X1) and the associate 0 volt is connected to (MX).
If there is not an associated 0 volt available then (MX) should be connected to the (G0) terminal.
To download the Forta Handbook please click HERE.
  • Field Devices
  • 7353