Field Devices - Cannot connect MD actuator to MBX valve, using appropriate linkage.
  • Field Devices - Cannot connect MD actuator to MBX valve, using appropriate linkage.
  • sesa125819
    sesa125819
‎2018-09-06 12:56 PM
Cannot connect MD20B-230 actuator to MBX4451 valve, using a 914-1071-000 linkage.
Field Devices
  • MD Actuator
  • MB valve
  • MBX valve
  • Linkage
The existing documentation is very unclear and shows the wrong bracket.
The issue arises initially in that a different bracket is shown in the current documentation.
The second issue is that there is a circlip on the back of the actuator which must be positioned before fitting the bracket. Below is a picture showing the correctly circlip and bracket. Please take note of the circlip position.
Revised documentation will be available in due course.
  • Field Devices
  • 6967
0% helpful (0/1)