Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Field Bus controller shows its version number as 0.000000

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Field Bus controller shows its version number as 0.000000
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Dave_Shore
    Dave_Shore
  • DavidFisher
    DavidFisher
  • BillNeville
    BillNeville
  • YangboLIU
    YangboLIU
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1990 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Field Bus controller shows its version number as 0.000000

Picard Product_Support
‎2018-09-06 01:37 PM

Last Updated: Dave_Shore Schneider Alumni (Retired) ‎2023-02-13 05:25 AM

Issue

Field Bus controller shows its version number as 0.000000.

Learn controllers from comm port is very slow and fails when reloading the controller. Updating the firmware will not fix this problem.

Product Line

Andover Continuum

Environment

  • Cyberstation 1.74 above
  • i2 controllers
  • B3 controllers

Cause

There are many reasons that will cause the i2 and B3 controllers show their version number as 0.0000000

  1. Wireless network enabled or Multi-Network card enabled on the machine.
  2. Database snatched from Flash RAM after power-cycle does not match to the Continuum Database
  3. Some controllers with special firmware (Such as B38XX-V with 4.501043) have points referenced by other controllers, this will make the source controller buffer to be full after more than 20 hours
  4. Unknown application software installed on the CyberStation PC
  5. B-Link fault will also cause this problem

Resolution

  1. Exit Continuum CyberStation, then ensure only a single network card is enabled
  2. Fix the problem caused by database mismatching:
    1. Create a new database and bring the master controller online,
    2. Do learn from the commport and bring the field controllers online
    3. Click the "Reset" button on the Runtime tag after opening the controller editor.
    4. Do database initialization and connect the original database to see if the version number is correct or not. If not, skip to item 4. If yes, do SendToController and then BackUpToFlash
  3. Update the controllers to the latest version.
  4. Rebuild the CyberStation PC. Only have the Windows operating system and Continuum CyberStation installed.
  5. Skip over B-Link and connect Field bus to BCX1 comm2 directly to verify B-LINK has some fault, and then replace it with new one, if required
Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 5538
  • DavidShore23
Was this article helpful? Yes No
0% helpful (0/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of