Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Failed Creation IDNLiveDataPtr Error when running Webpinpoint after a period of time

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Failed Creation IDNLiveDataPtr Error when running Webpinpoint after a period of time
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Alan_Wood
    Alan_Wood
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1821 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Failed Creation IDNLiveDataPtr Error when running Webpinpoint after a period of time

Product_Support
‎2018-09-11 07:08 AM

Issue

Webpinpoint runs for awhile then gives the error Failed Creation IDNLiveDataPtr

Environment

Windows 7

Windows Server 2003

Windows Server 2008

Cause

The IIS Resources are recycled after a period of time (default is 29 hours). This disconnects webpinpoint after this time.

Resolution

The Webclient Installation and Planning Guide describes this for Windows Server 2003

1. From the Windows Control Panel, double click and open Administrative Tools. The Administrative Tools dialog appears. Appendix A: web.Client Security and Troubleshooting Tips Andover Continuum web.Client Planning and Installation Guide 149

2. Double click and open Internet Information Services (IIS) Manager. The Internet Information Services (IIS) Manager dialog appears.

3. In the navigational directory, expand your local computer directory.

4. Expand the Application Pools directory.

5. Right click on DefaultAppPool, and from the popup menu, select Properties. The DefaultAppPool Properties dialog appears.

6. Select the Recycling tab.

7. Next to the Recycle worker processes (in minutes) checkbox, which should be checked, notice the field displaying the default number of minutes - 1740 minutes. This is equivalent to 29 hours.

8. To lengthen this time, use the field's up-arrow button to add minutes. (Use the down arrow to subtract minutes.)

9. Click OK. 

Windows 7/Server 2008 Similar steps as above with a couple differences because of the interface. 

In IIS Manager Select Recycling(Link in Actions Pane)
Deselect Regular Time Intervals in Minutes

In IIS Manager Select Recycling(Link in Actions Pane)

Deselect Regular Time Intervals in Minutes then Next then Finish

Select Advanced Settings(Link in Actions Pane)

Idle Time-out(minutes)

Set to 0 then Ok

Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 15887
  • create
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore