FTT-10 LONWorks Network Design Rules - LON Wiring Guidelines

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • FTT-10 LONWorks Network Design Rules - LON Wiring Guidelines
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
3 Likes
33004 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

FTT-10 LONWorks Network Design Rules - LON Wiring Guidelines

Picard Product_Support
‎2020-12-02 06:52 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:52 AM

Issue

Many LonWorks network installation problems can be avoided if the appropriate network design rules are followed when the network is being designed.

Product Line

TAC IA Series, TAC Vista, Satchwell Sigma

Environment

  • I/A Series MicroNet (LON) Controllers
  • Satchwell Sigma MicroNet series LON Controllers
  • Vista
  • Xenta Controllers

Cause

The I/A Series MicroNet System Engineering Guide (F-26507) was written as a resource of information for the installation of the I/A Series MNL-100, 200 & VAV controllers as well as the Sigma MicroNet 440 and 620 controllers.  The Resolution, below, is a summary of the LON design rules presented in this document.

Resolution

FTT-10 LON network wiring must be installed using Echelon-approved wire.  The most common type of wire used is described as Category 4  cable.  This wire is normally unshielded stranded twisted-pair 22AWG (0.65mm).  An example of this wire is the W221P or W222P series cable from Connect-Air International (http://www.connect-air.com).  This type of cable is normally available both in plenum rated and non-plenum rated types.  Consult the job specifications to determine if plenum-rated or shielded cable is required.

The LON network can be wired using "Free Topology" or "Bus Topology" wiring segments.  

1.  BUS Topology Guidelines

  1. BUS Topology LonWorks wiring extends from device to device (daisy chain format) with no branches or stubs.
  2. A LON-TERM-2 terminator must be installed at each end of the LON bus.
  3. When using standard Category 4 LON cable with the recommended terminators, the bus may be up to 4593 feet (1400 meters) in length.
  4. When extending LON wire to the MN-Sx sensor base in a bus topology network, the sensor base must be wired as part of the daisy chain and not as a stub connection.

2. FREE Topology Guidelines

  1. Free Topology imposes essentially no restrictions on the layout of the network -- some controllers may be wired point to point and others branching from a common point. 
  2. The free-topology LON network must be terminated at one point with a LON-TERM-1 terminator.
  3. When using standard Category 4 LON cable, the total wire length in a free topology LON network may not exceed 1641 feet (500 meters).  In addition, the longest wire path between any two controllers on a free topology LON network may not exceed 1312 feet (400 meters).

3. Common LON Network Wiring Guidelines

  1. LON wiring can not be part of an active bundled telephone trunk even if the telephone trunk is wired with Category 4 wire.
  2. Shielded Category 4 wire may be used in high EMI/RFI environments.  The shield must be wired continuously and grounded through a 470 Kohm resistor at one end.
  3. LON wiring must not be bundled with or housed in the same conduit as controller I/O and power wiring.

 4. LonWorks Network Wiring and Addressing Guidelines

  1. When the number of controllers on a LonWorks network exceeds 60, the network must be split into segments with not more than 64 controllers or devices per segment using LonWorks Repeaters or Routers. 
  2. When counting the controllers and devices on a LonWorks network segment, a LonWorks Network Interface Device and the repeater itself must be included in the device count in each segment.
  3. In a LonWorks network containing repeaters or routers, each LonWorks network segment must be properly terminated, as described above.
  4. Domain / Subnet / Node addressing is used when configuring the LON controllers.
  5. A LonWorks Subnet consists of a series of LonWorks controllers all configured within the same LON Subnet number.
  6. A single LonWorks Subnet can have a maximum of 127 device and controller Node addresses.  This Node address count includes the LonWorks Network Interface, all controllers on the subnet, and repeater and/or router node addresses.  An allowance is typically made for additional addresses to be used by LonWorks tools connected to the Subnet.
Labels (3)
Labels:
  • Satchwell BAS & Sigma
  • TAC IA Series
  • TAC Vista
Attachments
Tags (5)
  • Find more articles tagged with:
  • 7285
  • LeoTantalo20
  • PeterLarsen21
  • PeterLarsen25
  • RandyDavis22
Was this article helpful? Yes No
100% helpful (4/4)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore