Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Estimating Security Expert SQL database sizing

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Estimating Security Expert SQL database sizing
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • AdamSteele
    AdamSteele

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2678 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Estimating Security Expert SQL database sizing

AdamSteele Champion
‎2021-09-05 07:52 PM

Issue

How to estimate the disk space required to accommodate a given Security Expert installation.

Product Line

EcoStruxure Security Expert

Environment

  • Security Expert
  • Microsoft SQL Server

Cause

The Security Expert databases will grow in size depending on the configuration and logging requirements. Therefore, estimating how much a database will grow over time should be done to determine which Microsoft Database solution and hard drive requirements.

Resolution

  1. The Installation Guide does have some hardware recommendations under the System Requirements section, and these should be used as a baseline for allowing appropriate database storage.
    1. 10 controllers w/ 16 modules each - 40GB
    2. More than 10 controllers w/ any number of modules each - 100GB.
  2. The configuration database (SecurityExpert) is relatively small and will typically not grow much.
  3. The events database (SecurityExpertEvents) is what logs all events and alarms, and it will grow over time, rapidly depending on what is being logged and how often. There are many variables in play from one site to another. The space required for a standard Security Expert Database is dependent on, but not exclusive to:
    1. The amount of Inputs/Outputs/Readers you have with Log Events enabled.
    2. The amount of traffic through the site.
    3. The number of Expanders and other Records.
    4. The frequency of backups and purging of events from the SecurityExpertEvents database.
  4. As a guideline, we can broadly calculate storage requirements based on the size of each event being logged. Typically this will be 564 bytes per event. If you have 2000 Events per day, here is the calculation for how many MB will be used per day:
    1. 564 B x 2000 = 1128000 B = 1.07 MB per day
    2. If those events that are being logged are alarms as well, then this total would be doubled.
  5. Another way to calculate this is to take what a typical usage requirement would be for a site or monitor a live site over a week/month to calculate the sites' average usage and extrapolate that to fit.
    1. For example, a site with 130 doors being used 8 hours a day and with door openings and closings 10 times an hour would equate to just under 1GB a month. Please note these are very rough guesses; individual sites might be busier/quieter.
  6. Performing regular SecurityExpertEvents database backups and purges will ensure that the database size does not get too large for the installation.
    1. For instructions, see the System Backups section in the Installation Guide and AN 279 Security Expert Differential Backups.
Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (5)
  • Find more articles tagged with:
  • AdamSteele21
  • AdamSteele22
  • AdamSteele23
  • AdamSteele26
  • HernanUruena24
Was this article helpful? Yes No
100% helpful (4/4)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore