Esmi Ultima Integration – Troubleshooting Media Gateway Card Communication
  • Esmi Ultima Integration – Troubleshooting Media Gateway Card Communication
  • Sandeep_Kumar006
    Sandeep_Kumar006
Ensign Sandeep_Kumar006 Ensign
‎2025-08-29 01:08 AM
Last Updated: Administrator CraigEl Administrator ‎2025-08-29 01:11 AM
Warning
Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.
The Media Gateway Card is unable to send panel messages to the converter, which translates the panel language into Modbus/BACnet protocols.
ESMI Fire Detection.
FFSULH1007.
The TCP/IP port on the Media Gateway Card is not functioning correctly, impacting BMS integration with the panel.
  1. Check Firmware Version
    • Navigate to Engineer Options → System Information.
    • Ensure the LAN cable is connected to ETH 1 port.
    • ETH 0 should be set to DHCP.
    • Verify the firmware version:
      Expected version: S794_V01.109
  2. Firmware Update (if needed)
    • If the version is not visible or outdated, update the firmware.
    • Refer to this article:
      Esmi Ultima Media Gateway Card Firmware Update
  3. Configure Graphics / Third Party & VR Settings
    • Go to Engineer Options → Configuration → Panel Module → Media Gateway Card
    • Select Graphics / Third Party Settings and apply changes as per reference images.
    • Submit the settings.
    • Then go to VR Settings and apply changes as per reference images.
Outcome
After applying the above steps, the issue should be resolved
  • ESMI Fire Detection
  • SandeepKumar25