Error when attempting LonWorks communications in WorkPlace Tech: "Failed to get communications type, using LonWorks as default"
  • Error when attempting LonWorks communications in WorkPlace Tech: "Failed to get communications type, using LonWorks as defaul...
  • RyanSuar
    RyanSuar
‎2018-09-06 02:08 PM
When attempting LonWorks communications in WorkPlace Tech, the following error message is seen.
WorkPlace Tech 5.7.x
Echelon U10 USB LON Network Interface (part number ECH-75010) – TP/FT-10 Channel
WorkPlace Tech LonWorks communications is not properly initialised.
Re-initialise WorkPlace Tech LonWorks communications.
  1. In WorkPlace Tech, go to 'Tools' > 'Configure Communication'.
  2. Change the communications type to 'BACnet' and click 'OK'.
  3. Open up 'Configure Communication' again and change the communications type back to 'LonWorks'. This should re-initialise the LonWorks communications.