Issue
When attempting LonWorks communications in WorkPlace Tech, the following error message is seen.
"Failed to get communications type, using LonWorks as default"
Environment
WorkPlace Tech 5.7.x
Echelon U10 USB LON Network Interface (part number ECH-75010) – TP/FT-10 Channel
Cause
WorkPlace Tech LonWorks communications is not properly initialised.
Resolution
Re-initialise WorkPlace Tech LonWorks communications.
- In WorkPlace Tech, go to 'Tools' > 'Configure Communication'.
- Change the communications type to 'BACnet' and click 'OK'.
- Open up 'Configure Communication' again and change the communications type back to 'LonWorks'. This should re-initialise the LonWorks communications.