Error "Invalid Server Type" when attempting to log into the Project Configuration Server (PCS)
  • Error "Invalid Server Type" when attempting to log into the Project Configuration Server (PCS)
  • RobertAndriolo
    RobertAndriolo
  • LeeCravens
    LeeCravens
‎2018-09-11 10:08 AM
StruxureWare Building Operation 1.5 and newer
Attempting to log into the Enterprise Server IP and Port address with Workstation for Projects
Ensure that the Project Configuration Server is installed.
  1. Open Software Administrator and check that the Project Configuration Server tab is shown. If not then the server has not been installed. Install this first
  2. When using Workstation for Projects, make sure you use the correct port setting (HTTP or HTTPS) as defined in the Software Administrator
  • 16644