Issue
When you try to insert a new Xenta server into NL220 you receive the error message.
Environment
- NL220
- XBuilder
Cause
Controller Object names are limited to 16 character long.
Resolution
In X-Builder, under the SNVT folder, rename the Controller object names to less than 16 characters.