Error connecting to Xenta Server in browser using HTTPS

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Error connecting to Xenta Server in browser using HTTPS
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Benji
    Benji
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4392 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Error connecting to Xenta Server in browser using HTTPS

Picard Product_Support
‎2018-09-11 01:34 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 03:11 AM

Issue

After updating FireFox to version 34 and later, you get the message "Unable to Connect Securely" when accessing a Xenta Server using HTTPS

 

After updating Chrome to version 40 and later, you get the message "This webpage is not available" when accessing a Xenta Server using HTTPS

 

In Internet Explorer, you get the message "This page can't be displayed" when accessing a Xenta Server using HTTPS

Product Line

TAC Vista

Environment

  • Xenta Server
  • FireFox
  • Chrome
  • Internet Explorer

Cause

From version 34 of FireFox and version 40 of Chrome, SSLv3 is disabled by default for security reasons as SSLv3 is no longer considered secure enough. As per Vista Server Cryptographic Protocols TAC Vista, TAC Xenta Server and TAC Xenta 911 is using SSLv3 and is therefore blocked when using SSL (HTTPS).

In the newest versions of Chrome and FireFox, not even the work around described below works, so you need to set the Xenta Server to low security through the XBuilder project.

Resolution

In Internet Explorer, FireFox and Chrome you can manually reenable SSLv3.

 

Solution 1: Set the Xenta server to only use HTTP and not HTTPS

This is done in TAC XBuilder

 

Solution 2: Allow SSLv3 in FireFox

1: In the FireFox address bar, write about:config

2: Accept the warning

3: Write security.tls.version.min in the search field - below you can see the default setting

4: Double click the line, and change the number to 0

5: Try logging into the Xenta Server again. If it doesn't work the first time, restart the browser and try again

 

Solution 3: Allow SSLv3 in Internet Explorer

Check the advanced settings in Internet Explorer. SSL 3.0 must be enabled. If it's not, then enable it. If you can't, it's because it's disabled by a policy, and you need to get the IT department to enable it.

 

Solution 4: Allow SSLv3 in Chrome

1: In the Chrome address bar, write chrome://flags/#ssl-version-min and select SSLv3 in the drop down box.

Solution 2: Allow SSLv3 in FireFox

1: In the F

Labels (1)
Labels:
  • TAC Vista
Tags (4)
  • Find more articles tagged with:
  • 17372
  • err_ssl_version_or_cipher_mismatch
  • ssl3
  • ssl_error_no_cypher_overlap
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore