Error comm port is not enabled applying an Xdriver file to comm2 on a BCX
  • Error comm port is not enabled applying an Xdriver file to comm2 on a BCX
  • Alan_Wood
    Alan_Wood
‎2018-09-06 02:20 PM
An error is received, comm port is not enabled when trying to apply the 2nd generation xdriver file to comm2 on a BCX.
  • Continuum 1.9x
  • BCX4040
  • Xdriver
Typically comm2 is set to mstp. Trying to apply the Xdriver file to the comm port thinks it already has the port applied and renders the error.
  • Pull the battery connection
  • Power off the controller which sets the port to autoset
  • Power up the controller
  • Set comm2 to xdriver and apply the file and no error is received
  • -If this still doesn't work then update the firmware, it may resolve the issue
If this does not resolve the issue try Clearing Database Backup from the controllers webpage and reload.
  • 4236