Error: NS #52 IcaErrNsDuplicateNode
  • Error: NS #52 IcaErrNsDuplicateNode
  • Cody_Failinger
    Cody_Failinger
‎2018-09-06 03:27 PM
An attempt was made to add a node that is already defined. Received the error: The device is already defined. (Subsystem: NS, #52)
  • NL220
  • LonMaker
  • Vista
  • LNS
A device in the TAC network has been assigned the same neuron ID previously as the device that is attempting to be downloaded.
In the system plug-in:
  1. In the TAC network pane, delete the Xenta group that the controller belongs too.
  2. Update the TAC network.
  3. Download the controller again.
  • 8113