Erasing NOVRAM from ASCs
  • Erasing NOVRAM from ASCs
  • sesa139513
    sesa139513
  • Roger_Bently
    Roger_Bently
‎2018-09-06 03:09 PM
I/NET Seven Site
How to erase the firmware and programming in the ASC
There is a way for users to erase the firmware and programming in the ASC by following the following steps:
Note: take care that you do not clear the memory on a stand-alone ASC with no SLI or I/NET computer with which to perform step 6! This procedure does not just reset the parameters, it removes the entire application.
  1. Remove power from the ASC.
  2. Place DIP Switches 6-12 in the off (0) position.
  3. Apply power to the ASC, and then remove power again.
  4. Place DIP Switches 6-12 in the on (1) position.
  5. Apply power to the ASC.
  6. Download the UPD file by selecting Update ASC to restore it to defaults.
On occasion, it may be necessary to repeat steps 1-5 twice.
  • TAC INET
  • 1833