Epibuilder Dynamic Text fields not displaying in a badge layout, error encountered while trying to update custom attributes or Error Opening EpiDesigner Configuration Database

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Epibuilder Dynamic Text fields not displaying in a badge layout, error encountered while trying to update custom attributes o...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Alan_Wood
    Alan_Wood
  • Clifton_eakes
    Clifton_eakes
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2708 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Epibuilder Dynamic Text fields not displaying in a badge layout, error encountered while trying to update custom attributes or Error Opening EpiDesigner Configuration Database

Picard Product_Support
‎2018-09-07 03:20 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-11-19 07:09 AM

Issue

Epibuilder Dynamic Text fields are not displaying in a badge layout or Errors related to EpiBuilder or EPIDesigner

Product Line

Andover Continuum

Environment

  • EpiBuilder
  • Badge Layout
  • Cyberstation

Cause

Install didn't make the connection properly or badging wasn't enabled during the initial Continuum installation or Windows permission restrictions 

Resolution

  1. From Make Edit badge in Continuum, Open Badge layout in EpiBuilder (If you have a problem opening Badge Layout see Note #2 below)
  2. View Options> Data Fields
  3. Select Use the data fields defined in a database
  4. If nothing is there, click the Other Database button
  5. Select Use an ODBC database
  6. Select the Data Source button
  7. Select System DSN tab and then select EPISDK then OK
  8. Click the Select button add the path to SDKNoDB.mdb (C:\Program Files\Continuum\EpiBuilder\Data)
  9. Click Open, Click OK
  10. All fields should now be available or the error should no longer happen on startup

If receiving: ** Error Opening EpiDesigner Configuration Database error when selecting MakeEdit Badge, 

ErrorOpeningEpiDesignerConfigurationDatabase.png

 

Note #1: Permissions can affect the configuration of the Data Sources. If some options aren't configurable or have been changed from the default like buffers are not set to 2047 then try the configuration with increased permissions.

Start>run odbc32.exe and check that the System DSN had EPISDK, If not, add it and then follow the instructions able to set the SDKNoDB.mdb 

If the site is utilizing hard drive encryption on the hard drive.  Move the sdknodb.mdb to an unencrypted network share to correct the errors after updating the episdk datasource. 

Note #2:  If you cannot perform step #1 from above check the following:

On a 32 bit system run the following command from either the run window:  odbcad32.exe and check that the User DSN has an EPISDK entry with the datasource set to SDKNoDB.mdb . 

The file should be located at the following path: C:\Program Files (x86)\Continuum\EPIBuilder\Data\

On a 64 bit system run the following command from either the run/search window:  C:\Windows\SysWOW64\odbc32.exe and check that the User DSN has an EPISDK  entry with the datasource set to SDKNoDB.mdb .

The file should be located at the following path: C:\Program Files (x86)\Continuum\EPIBuilder\Data\

Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 3987
  • integrated
Was this article helpful? Yes No
0% helpful (0/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore