Issue
Product Line
TAC IA SeriesEnvironment
I/A Series R2
Cause
Resolution
Use one of the following program objects available in the Niagara library:
-
Psychrometric Calculations Object
- Location:
tridiumx/lib/programObjects/hvac/Psychrometric Calculations.sns - Function:
Calculates enthalpy, wet bulb, and dew point using inputs of dry bulb temperature and relative humidity. - Requirement:
lib.jarfile must be present in the station.
- Location:
-
Outside Air Optimization Object
- Location:
tridiumx/lib/energyManagement/OutsideAirOptimization.sns - Function:
Compares two sets of temperature and humidity inputs to determine the air supply with the least heat load.- Supports temperature or enthalpy comparison.
- Includes free cooling logic and low-temperature protection.
- Location: