Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Enterprise Server station upgrade failure from I/A Series R2 version 529 to 532

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Enterprise Server station upgrade failure from I/A Series R2 version 529 to 532
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RyanSuar
    RyanSuar
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1221 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Enterprise Server station upgrade failure from I/A Series R2 version 529 to 532

Picard Product_Support
‎2018-09-06 12:16 PM

Issue

Enterprise Server station upgrade failure from I/A Series R2 version 529 to 532. The station in version 529 was successfully converted from DB to XML format. The following error was seen when converting the station from XML to DB in version 532.

ERROR: c:\niagara\r2.301.532\stations\\config.xml (7270,149) : Unknown class "tridiumx.commercialCooking.CommercialCookingService". Parse of XML failed.
 

Environment

I/A Series r2.301.529 and earlier
I/A Series r2.301.532

Cause

When you create a new station as a server station in I/A Series R2, you will normally select the option 'Is this station going to be a server?' checkbox in the New Station Wizard. When you make this selection, the Backup Service and the Database Service which are needed by a server station will be automatically selected.
In versions r2.301.529 WorkPlace Pro and earlier, the Commercial Cooking Service is also automatically selected, so this should be unchecked since this is not being used. However, if you did not uncheck the Commercial Cooking Service, the Enterprise Server station will still run and work normally.

In I/A Series version r2.301.532, the Commercial Cooking module is no longer available and is not installed during the installation of the I/A Series software. The error will occur if you try to convert the station database from XML to DB in version 532 because the database contains the Commercial Cooking Service which does not have a corresponding module.

Resolution

In I/A Series version 529, you should remove the Commercial Cooking Service from the station before you perform a conversion from DB to XML format.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 8073
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.