Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Enterprise Server does not start when computer is rebooted or shuts down right after starting it

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Enterprise Server does not start when computer is rebooted or shuts down right after starting it
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • sesa139513
    sesa139513
  • Derrick_Ratliff
    Derrick_Ratliff
  • Benji
    Benji
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
7306 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Enterprise Server does not start when computer is rebooted or shuts down right after starting it

Picard Product_Support
‎2018-09-06 01:09 PM

Issue

Enterprise Server does not start when computer is started/rebooted or shuts down right after starting it

StruxureWare Building Operation Software Administrator log shows the following error:

nsp.NspServer The server has made too many unsuccessful attempts to start...

Product Line

EcoStruxure Building Operation

Environment

  • Software Administrator
  • Enterprise Server

Cause

StruxureWare Building Operation is prohibiting the Enterprise Server from starting up because the ES has exceeded the number of startup retries defined in server_startup.properties.

When the server_startup.properties file is opened in a text editor, the first line indicates a startup failure.

NspServer.Startup.Service.Status: fail

Resolution

Windows XP: This is caused by a dependency, set in the registry, on the service netprofm (Network List Service), which exists on Windows Vista and later, but not on Windows XP.

The error has been verified on a new installation of Windows XP. Steps 1 and 2 below help to resolve this on the XP operating system.

Windows 7 and Windows Server 2008 R2 including Virtual:

  1. Start ES manually from the Software Administrator. If this fails, the log in the Software Administrator explains why.
  2. Start the ES manually from the Services listed in Services (Start, My Computer, right-click, Manage, Services click the + to find Services) find StruxureWare Enterprise Server
  3. Go to the Software Administrator and modify the HTTP, HTTPS, and TCP ports to available ports. (suggested: 81, 444, & 4444).
  4. The number of startup retries is defined in the following file:
    1.2.0 and below : C:\Program Files\Schneider Electric\StruxureWare X.X\Enterprise Server\etc\server_startup.properties
    1.3.0                  : C:\Program Files\Schneider Electric StruxureWare\Building Operation X.X\Enterprise Server\etc\server_startup.properties
    1.4.1 and above : C:\ProgramData\Schneider Electric StruxureWare\Building Operation X.X\Enterprise Server\db\etc\server_startup.properties
    Increasing this threshold in server_startup.properties will allow the Enterprise Server to have a better chance of achieving a successful startup.

    server_startup.properties -- Original settings
    NspServer.Startup.Service.Status: fail
    NspServer.Startup.Service.Status.NbrOfConsecutiveFails: 2
    NspServer.Startup.Service.Status.QuitRetryAfterNbrOfConsecutiveFails: 2

    server_startup.properties -- Threshold increase to 10 retries.
    NspServer.Startup.Service.Status: success
    NspServer.Startup.Service.Status.NbrOfConsecutiveFails: 0
    NspServer.Startup.Service.Status.QuitRetryAfterNbrOfConsecutiveFails: 10
     
  5. Last option, and please go through all the previous steps mentioned before attempting: Open regedit and go to HKEY_LOCAL_MACHINE\SYSTEM\ControlSet001\Services\Building Operation X.X Enterprise Server. Open the DependOnService and remove the first line (netprofm) and then reboot. The ES will now start automatically.

 


 

Alternative Workarounds

  1. Go to Computer Management by right clicking on Computer and going to Manage.
  2. In Computer Management, go to Services and Application > Services > Building Operation X.X Enterprise Server. Right click on Building Operation X.X Enterprise Server and go to properties.
  3. The two different settings that can be changed so that the Enterprise Server starts automatically as a service after a reboot are as follows.
    1. Under the General tab, change the Startup type from Automatic to Automatic (Delayed Start).
    2. Or under the Recovery tab, change the Restart service after to a value of 3 or more minutes.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • 6535
  • mode
  • warmstart
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore