Enterprise Server (ES) taking a long time to perform shutdowns

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Enterprise Server (ES) taking a long time to perform shutdowns
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1367 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Enterprise Server (ES) taking a long time to perform shutdowns

Picard RobertAndriolo Picard
‎2021-06-16 07:43 PM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:34 AM

Issue

  • ES takes up to 30 minutes to perform a shutdown.
  • Trace log contains multiple entries indicating
    • "Subscription service forcefully shutting down; [sub-server name]" 
    • "Subscription service forcefully shut down; [sub-server name]"  
  • A secondary issue - When performing Windows Updates automatically, Windows attempts to shut down all running services within one minute which can end the Enterprise Server service prematurely

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Server 3.1.x and below
  • Large Multi-server installation 

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

 

Cause

During a shutdown procedure of the Enterprise Server a call to every sub server is made to remove subscriptions. However, the thread pool that executes these commands may already be stopped and the server then waits the 15 seconds timeout period prior to moving to the next item.  On a large 100+ multi-server installation, this 15 second delay can accumulate to a lengthy shutdown period.  

 

The trace log will contain the messages shown  in the issue and the 15-second delay between each server 

Enterprise Server Trace log messages seen during shutdown showing the 15-second timeout delay.Enterprise Server Trace log messages seen during shutdown showing the 15-second timeout delay.Enterprise Server Trace log messages seen during shutdown showing the 15-second timeout delay.

Resolution

Upgrading to 3.2.2 (and above) will rectify the timeout issue provided that the subscription thread pool has already stopped.  These versions now ignore the 15-second timeout for each sub-server if the thread pool has already stopped.  


It is possible to extend the Windows service shutdown time by adding or adjusting a registry entry called WaitToKillServiceTimeout

.  

To change the timeout:

  1. Start the registry editor (“Regedit”)
  2. In the tree on the left, navigate to:
    HKEY_LOCAL_MACHINE\SYSTEM\CurrentControlSet\Control
  3. In the right panel, find the WaitToKillServiceTimeout value. If you don’t see it, create it by:
    1. Selecting Control on the left
    2. Choosing Edit > New > String Value (not DWORD) from the menu
    3. Naming the new value WaitToKillServiceTimeout.
      waittokillservicetimeout-registry-value.png
  4. Double-click the WaitToKillServiceTimeout entry to bring up the Edit String window.
  5. Enter a numeric value (e.g. 60000) in the Value data field in milliseconds and click OK to save your change.
    change-waittokillservicetimeout-value.png

  6. Reboot your computer. The new timeout setting will not take effect until Windows restarts.

Note that this modification will not make Windows wait indefinitely for your service to finish. If your service takes longer than the entered time (in this example 60 seconds), it will still be terminated. Be sure to choose a timeout value that is long enough to cover your scenario, but not too long to make shutdown time intolerable.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • RobertAndriolo21
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore