Issue
Unable to determine whether the Enocean device in hand is compatible with MPM controllers
Unable to add more devices to a MPM controller
Product Line
EcoStruxure Building Expert
Environment
Multi-Purpose Manager
Cause
Some pre-configured icons in the "Add Devices" list have a name but do not have a specified Enocean profile or vice versa.
Resolution
The Following devices are embedded in the MPM firmware and require no scripts to integrate with an MPM. All Devices in the below list (except for Enocean relay) are outbound devices (i.e. devices that are only able to send telegrams to other devices)
| MPM Sub-device list | Description | Compatible Schneider-Electric Products |
| CO2 Sensor A5-09-04 | CO2 Sensor | SR04 CO2 (LSS442510) (868MHz) |
| Door/Window Sensor D5-00-01 | Single Input Contact | SED-WDS-U-5045 (902MHz) 10020032 (LSS10020032) 10020042 (LSS10020042) 10020047 (LSS10020047) |
| Double Rocker Switch F6-02-01 | Light and Blind Control – Application Style 1 | EDRPU-W-EO (902MHz) 10020048 (LSS10020048) (868MHz) |
| Enocean Relay | Inbound profile | |
| Enocean Switch | Light and Blind Control – Application Style 2 | ESRPU-W-EO (902MHz) 10020049 (LSS10020049) (868MHz) |
| Enocean Thermostat | Obsolete | |
| KeyCard Switch F6-04-01 | Key Card Activated Switch | SED-KCS-U-5045 (902MHz) |
| Light Sensor A5-06-01 | Light Sensor Range 300lx to 60.000lx | 10020047 (LSS10020052) |
| Light Sensor A5-06-02 | Light Sensor Range 0lx to 1.020lx | SED-LLS-U-5045 (902MHz) LSS10020053 (868MHz) |
| Motion Sensor A5-07-01 | Occupancy Sensor with Supply Voltage monitor | SR-MDS Bat SED_CMS_U_5045 (902MHz) |
| Thermostat A5-02-05 | Temperature sensor Range 0°C to +40°C | SED-T00-U-5045 (902MHz) 10020046 (LSS10020046) 10020033 (LSS10020033) |
| Thermostat A5-04-01 | Temperature & Humidity sensor Range 0°C to +40°C and 0% to 100% | SED-TH0-U-5045 (902MHz) 10020041 (LSS10020041) SR04 rH |
| Thermostat A5-08-01 | Light, Temperature and Occupancy sensor Range 0lx to 510lx, 0°C to +51°C and Occupancy Button | SR-MDS |
| Thermostat A5-10-03 | Room Operating Panel: Temperature Sensor and Set Point Control | SR04 P (LSS226172) |
| Thermostat A5-10-05 | Room Operating Panel: Temperature Sensor, Set Point and Occupancy Control | SED-TS0-U-5045 (902MHz) |
| Thermostat A5-10-10 | Room Operating Panel: Temperature and Humidity Sensor, Set Point and Occupancy Control | SED-THS-U-5045 (902MHz) |
| Thermostat A5-10-12 | Room Operating Panel: Temperature and Humidity Sensor and Set Point | SR04P rH(LSS252331) |
| Thermostat A5-10-19 | Room Operating Panel: Humidity, Temperature Set Point, Temperature Sensor, Fan Speed and Occupancy Control |
-The maximum number of devices added to each MPM is 49
-The maximum number of EnOcean devices added to each MPM is 49
-The maximum number of EnOcean devices with the same EEP added to each MPM is 49 .This only applies to firmware 2.13.1 and later, the limit for previous firmwares is 20. An Exception is the following limits for devices/widgets per MPM
- 20 EnOcean Switches
- 20 EnOcean Relays
- 4 EnOcean Thermostats
The Devices in the next table do not have a pre-configured icon in the devices list, however, scripts can be used instead and can be found below (Please read PDF first)
| Enocean profiles supported in script | ||
| EnOcean Equipment Profile (EEP) | Description | Example of Compatible Devices |
| (EEP A5-38-08) | Central Command Gateway |
Plug-in 15 Amp 120V 902Mhz 5-Wire 6A Relay 24V 902Mhz |
| (EEP A5-11-01) | Lighting Controller | 15A-20A 120/277/347V 902Mhz (inbound profile: A5-11-01) 15A 120-277V 902Mhz (inbound profile: A5-11-01) |
| (EEP A5-10-04) | Temperature Sensor, Set Point and Fan Speed Control | Thermokon SR04PS |
| (EEP A5-02-14) | Temperature Sensor Range -20°C to +60°C | Thermokon SR65TF |
| (EEP F6-03-01) | 2 to 4 Rocker Switch (Light and Blind Control) | Push-button, 2-gang |
| (EEP A5-20-1) | Battery Powered Actuator | Thermokon SAB02/SAB05 |
| Din Relay 1 channel (inbound profile: F6-02-02) |
||
| PWM 230V valve driver (inbound profile: A5-02-05) PWM 24V valve driver (inbound profile: A5-02-05) |
||