Endura DVR missing the Video in I/NET Seven Rev 2.41

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Endura DVR missing the Video in I/NET Seven Rev 2.41
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • sesa119952
    sesa119952
  • Tom_Poovey
    Tom_Poovey
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1921 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Endura DVR missing the Video in I/NET Seven Rev 2.41

Picard Product_Support
‎2018-09-06 01:20 PM

Issue

Endura DVR missing the Video in I/NET Seven Rev 2.41

Product Line

Pelco, TAC INET

Environment

  • I/NET Seven rev 2.41
  • Endura DVR

Cause

The Endura Workstation software that comes with the DVR (by default) is set to "Multicast". If this has not been changed, then you DO NOT have to change the three I/Net files listed below.

If the Endura Workstation software was changed from the default (Multicast) setting to a "Unicast" setting. Then you WILL have to change the three I/Net files listed below.

What is the Pelco definition of “Multicast” mode?

By default, Endura encoders and Pelco network IP cameras are default to stream live video in Multicast mode. A common symptom of multicast routing issue is where the date and time stamp can be seen on the workspace but the video is black. This symptom is commonly associated in a layer 3 routing network where appropriate multicast routing protocol has not been enabled globally or inside the VLAN.

Resolution

The resolution is to modify three files that are installed with I/NET Seven rev 2.41. These three files are located in this directory on the PC – C:\Program Files\INet Seven

  1. INetAMT.exe.config
  2. INetCfg.exe.config
  3. INetW.exe.config

Note: If the above three files are not in the I/Net folder, then you have not delete the previous SDK driver. You must delete the previous driver thru the "Add and Remove" option in Control Panel. Once removed then go into the I/Net CD and select the "Support" folder and manually load the new SDK Driver. Then proceed with the rest of the process in this article.

Use Notepad to open each one of these files one at a time and change this setting from the "default" of "False" to "True."

  1. After making all of the changes in the three file, shut down the I/NET and IO Server ICON.
  2. Restart the I/NET again, and the Video should show up in the I/NET program
Labels (2)
Labels:
  • CCTV
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 6197
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore