Emailing alarms if Microsoft Outlook is not used on the site?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Emailing alarms if Microsoft Outlook is not used on the site?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2702 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Emailing alarms if Microsoft Outlook is not used on the site?

Picard Product_Support
‎2018-09-07 11:42 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:40 AM

Issue

Emailing alarms if Microsoft Outlook is not used on the site?

Product Line

Andover Continuum

Environment

  • Continuum Cyberstation 1.73 and above
  • bCX 4040
  • Netcontroller II (9680)
  • ACX57xx Series (ACX II)

Cause

The customers site IT system is unable to provide reliable Email communications from Microsoft Outlook on the Continuum Workstations.

Resolution

The documented Outlook support:
Initially Full Microsoft Outlook or Microsoft Exchange was specified as the requirement
1.92 to 1.94 specified Microsoft Outlook 2007 for Windows XP and Vista (Full Microsoft Outlook or Exchange)
1.94sp1 to 2.03 specified Microsoft Outlook 2007 Microsoft Outlook 2010 (Full Microsoft Outlook or Exchange software package)

 

For further information on outlook versions see the KB article Outlook 2007 and Outlook 2010 with Continuum email alarms.

Notes

  • Only 32bit Outlook was tested/supported
  • Continuum does not support MS Outlook Express for emailing alarms
  • From v2.0 CyberStation has internal SMTP email options see  SMTP Email Alarm Configuration in Continuum 2.00 to 2.03

There are other email option for emailing directly from controllers.

There is a feature in the bCX (also NetController II, ACX II) controllers to be able to email messages directly to a SMTP server either manually or via Plain English programs, although this is not directly linked to the Continuum Alarm system and would require a Plain English program to determine what emails are to be sent.

See the "bCX1 Controller Technical Reference" Commissioning section for details on how to set up the controller to send out emails to a 3rd party SMTP email server. 

There is also the Continuum SNMP Configuration guide for use with SNMP alarming with a Network Management System.

Then in the CyberStation online help see the "SendEmail" function help on how to use Plain English to get the bCX (Netcontroller II or ACX II) to send out messages via email.

 

Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 4338
  • DavidShore22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore