Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

EWS Alarms from PME do not fully show the Source of the Alarm in EBO

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • EWS Alarms from PME do not fully show the Source of the Alarm in EBO
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidChild
    DavidChild
  • David_Kendrick
    David_Kendrick

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2123 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

EWS Alarms from PME do not fully show the Source of the Alarm in EBO

Admiral David_Kendrick Admiral
‎2020-08-11 01:11 AM

Last Updated: Picard RobertAndriolo Picard ‎2020-08-11 04:36 PM

Issue

Power Monitoring Expert (PME) is able to make its data objects and alarms visible to EBO via EcoStruxure Web Services (EWS). But when viewed, the Alarms from these EWS objects only shows a number rather than its actual object name in PME.

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Server
  • EWS Integration

Cause

There are two stages to bringing data via EWS into EBO.  The first is to create the EWS interface in EBO so that the EWS source (in this case PME) can be discovered.  However, if those discovered EWS objects are not then hosted in EBO, the Alarm Source details will be not complete.

Resolution

1. First Identify an object in PME which is also in Alarm and will also be Alarming in EBO when hosted. The date and time of the actual Last Occurrence can be useful here.

pme1.png

2. Notice that the Source name and Source of the same Alarm in EBO is only a number. In this case 3 or EWS Client/3.

pme2.png

3. Now select Host EWS objects from the EBO Menu and host that point or controller onto the EWS interface

pme3.png

4. Note now that all Alarm references previously showing just a number now immediately update with the correct Source name and Source now that the point has been hosted in the EBO Database. 

In this case PDU_2B_1_6A_ION9200

pme4.png

Note:At this point it would be very easy to simply decide to Host the entire PME Server onto the EBO Interface rather than a single object or controller as this would then update the sources of all alarmed objects.  However care must be taken that at this point not to overload the system.  Every hosted object will then be polled for value and alarm status periodically adding greatly to the comms between the PME and EBO systems and while the polling rate for Value and Alarm can be adjusted to sensible values there is an argument to only host those EWS objects that data is required from.

pme6.png

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • DavidKendrick20
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore