Issue
After an Upgrade to an Automation Server controller, the Requested values of some outputs and actual values do not match.
Product Line
EcoStruxure Building Operation
Environment
- Enterprise Server
- Workstation
- Automation Server with I/O Modules
Cause
The upgrade process somehow has caused some issues with the comm between the AS with I/O modules and the Enterprise Server/Workstation.
Resolution
Perform a cold start on the AS.