Drayton DC1000 and DC1100 differences
  • Drayton DC1000 and DC1100 differences
  • sesa125819
    sesa125819
‎2018-09-10 06:20 AM
DC1000
DC1100
What are the differences between the DC1000 and the DC1100?
The DC1000 was the predecessor of the DC1100, and therefore their functionality is very similar. From the information below it can be seen that the main difference is that the DC1000 had only one boiler output and had a "System On" output. The DC1100 has two boiler outputs and therefore can sequence the boilers, but it does not have a "System On" output.
It should be noted that the Remote Communications module is no longer available.
For the DC1000 data sheet please click HERE.
For the DC1100 data sheet general please click HERE, and for the DC1100 data sheet "A" please click HERE.
DC1000
DC1100
  • Field Devices
  • 7542